lead calcium battery

Submitted: Wednesday, Feb 04, 2009 at 20:13
ThreadID: 65702 Views:5300 Replies:8 FollowUps:15
This Thread has been Archived
Advice needed. Because I'm not very happy with the Hi-Tec Baintech battery charger, I am building my own smart charger. I am using an Electro PV Charge Controller, Model SBC-7130 and a switchmode 30amp power supply. What is the ultimate charge rate for a lead calcium battery? Some say boost rate should be 14.3, float 13.8 volts, some say boost rate 14.6, float 14 volts. Which one is correct or should they be higher? Thank you for your help.
Back Expand Un-Read 0 Moderator

Reply By: _gmd_pps - Wednesday, Feb 04, 2009 at 20:24

Wednesday, Feb 04, 2009 at 20:24
http://www.batteryuniversity.com/partone-13.htm
AnswerID: 347569

Reply By: Bushtrek - Wednesday, Feb 04, 2009 at 21:02

Wednesday, Feb 04, 2009 at 21:02
Have a couple of Supercharge Pb/Ca batteries in the truck.
The sticker on the top says ... Max Recharge Volts = 14.8, Float Voltage =14.0 max.

cheers
AnswerID: 347576

Reply By: Isuzumu - Wednesday, Feb 04, 2009 at 21:03

Wednesday, Feb 04, 2009 at 21:03
On my lead calcium batteries (SuperCharge Gold) it says not to charge over 14.8 volts

Cheers Bruce
AnswerID: 347577

Reply By: ABR - SIDEWINDER - Wednesday, Feb 04, 2009 at 21:08

Wednesday, Feb 04, 2009 at 21:08
Hi Lunchbucket

Just a warning.

Most solar regulators regulate by shorting out the solar panel. If your SBC-7130 does this it will burn out and possibly also burn out the 30A power supply.

Regards

Derek from ABR
AnswerID: 347580

Follow Up By: lunchbuckett - Wednesday, Feb 04, 2009 at 21:20

Wednesday, Feb 04, 2009 at 21:20
Derek thank you fore that advise it says pv panel open circuit voltage =17-23v short circuit current 32 amps-sbc-7130 . so this is not to good for me.
0
FollowupID: 615766

Follow Up By: ABR - SIDEWINDER - Wednesday, Feb 04, 2009 at 21:30

Wednesday, Feb 04, 2009 at 21:30
Use a 5A or 10A fuse between the two and if it blows you can't use it.

0
FollowupID: 615767

Reply By: Grungle - Wednesday, Feb 04, 2009 at 21:27

Wednesday, Feb 04, 2009 at 21:27
Does the Solar reg have a configurable current limit or can you current limit the power supply?

If not then you will keep tripping the units or blowing fuses because during boost, the solar reg sucks max current and if the power supplies current rating is higher than the regs current rating then you will blow the fuse on the reg. If the reg has a higher current rating than the power supply then you will blow that fuse. A solar panel can handle providing max current no worries because of their short circuit rating but any other basic power source can't.

I have tried this setup in depth and the only way around it was to use a Plasmatronic PL regulator which you can manualy set the current limit or by using a good power supply with manual current limit (I have a rhode and schwarz).

Also you need a power supply that can provide good current at around 15V plus which few do (except the expensive ones). This is so you can get the reg to actually go through its charge stages of boost and absorbtion which is around 14.5 - 14.8V (float doesn't matter because it's voltage is around 13.5V which most power supplies can do) . Panel voltage (open circuit) is typically around 19V so this is not a problem.

My first attempt overcame this by using a 300VA toroidal transformer with 18v - 0v - 18v windings @ 16.5A but you still need to current limit it.

My old setup can be read here -> http://www.grungle.com/solar.html

Regards
David
AnswerID: 347582

Follow Up By: lunchbuckett - Wednesday, Feb 04, 2009 at 21:44

Wednesday, Feb 04, 2009 at 21:44
David thanks for your help power suply voltage 11-14.06 volts@ 35 amps controller 12-16.5 volta @30 amps does this help
0
FollowupID: 615771

Follow Up By: RV Powerstream P/L - Friday, Feb 06, 2009 at 07:53

Friday, Feb 06, 2009 at 07:53
Grungle
That is an interesting concept as I have been looking at a simple control of solar at say a constant 15V to allow solar to be connected to a Sterling BB121250 as then the unit can accept all DC Power sources up to 15.5V before safety shut down.

I thought of using an MPPT but cannot get one without the charging algorithms and would be too costly in standard form.

By overcoming the maximum voltage supply the BB12150 can then accept Solar along with alternator power and also any old style transformer charger and turn them into a smart charger.

Ian

0
FollowupID: 615987

Follow Up By: Grungle - Friday, Feb 06, 2009 at 09:06

Friday, Feb 06, 2009 at 09:06
Hi lunchbuckett,

It doesn't matter what the voltage range of the reg is but instead what the settings are for the charge algorithyms. i.e boost - 14.4V for example. This is because during boost, the reg provides max current from the source (panels or power supply) until it reaches 14.4V (example). It then holds it at this voltage for a couple of hours during absorbtion and then goes to float.

If the power supply cannot get to the regs boost / absorbtion voltage then it may take a lot longer to charge the batteries. Different regs may do different things so connecting things up and trialing will reveal what yours will do.

At the end of the day however, a power supply that provides max continuous current (key words here) in the 14V range will be pretty good however you will find most will drop their voltage at high currents (i.e. the power supply has a max voltage of 14.1V but as you load it up and start increasing the current draw from it, its voltage drops to say 13.6 - 13.8V or even lower).

If I were you I would only ever consider taking around 20A from the supply to keep the heat down and voltage up. Also you don't say if you have current limiting on the power supply. If it is fused (try putting in a smaller fuse of say 20 - 25A for a 35A power supply), connect it up to the reg and turn it on and see what happens. You will most likely hear a pop as the fuse goes on either the supply or the reg (make sure it is fused as well before doing this).

You can build a simple current limit for the power supply with a pot and some sort of high current FET arrangement. There are plenty of circuits on the web detailing this.

Regards
David
0
FollowupID: 615995

Follow Up By: Grungle - Friday, Feb 06, 2009 at 09:26

Friday, Feb 06, 2009 at 09:26
Hi Ian,

I can't take credit for this concept at all though I have thought about it for many years but wasn't inspired to get off my butt until reading Rays efforts (link is on my Solar page).

To get the higher voltages, you will have to go with something with a toroidal transformer as opposed to a standard one. For an increase in current you could go 2 toroidals.

If you had a regulator that has a configurable current limit then you could connect it up to pretty much any power supply such as an alternator without worrying about damaging equipment.

However, a regulator of 30A or above would be more benificial as alternator charging puts in about 30A initially and then tapers off slowly as the batteries voltage increases. With the reg, it will draw a constant 30A until the boost / absorbtion voltage is met so you make more efficient use of the your alternator (not too sure about these ultra modern alternatoers though).

I find that I cannot get anymore than 30A from the alternator. At this time of year (yesterday was one of those days) we head up to solar sites for the QAS and QFRS because of low battery alarms. We connect up the car to the batteries (2V / 1000AHr x 6) to get some charge back in but we always have a Fluke clamp meter attached and find that 30A is the maximum the batteries will get (Navara and a Triton) regardless of revs.

I haven't had much experience with the MPPT but you should be able to make adjustments on the boost / absorbtion and float voltages due to the many different types of batteries out there. I will check with our supplier to find out if this is the case.

Regards
David
0
FollowupID: 615998

Follow Up By: RV Powerstream P/L - Friday, Feb 06, 2009 at 18:14

Friday, Feb 06, 2009 at 18:14
David
Im running 2v x1000AH 24 Volt and charging them with a toroidal transformer charger with an excellent algorithm.

I lift the bank with a crane and take it to work places.

Recently I ran at 25A recharge using a 1700is Subaru Inverter generator and got 6.5 hours out of the Subie.

If I ran it at 20A it would have run on echo and got around 11 hrs.

You can do that with a toroidal transformer charger but not a switchmode charger.

I dont know what your 2 Volt cells are but mine are Energel and they can be charged at 29.6V and can take it flat out with temperature compensation.

If you had the same batteries in your 12 V configuration you could boost your alternator voltage to 14.7 and achieve greater charging without the cut back normally produce from astandard alternator.

The MPPT Solar reg use a transformer but like I said not without the charging algorithms.
Ian
0
FollowupID: 616097

Follow Up By: Grungle - Friday, Feb 06, 2009 at 20:28

Friday, Feb 06, 2009 at 20:28
Hi Ian,

Wow, that is some serious capacity there!

We use either Concord 2V 915Ahr Batteries which are my preffered battery of choice as they have the highest charge cycles vs battery life (3000-6000 cycles compared to 300-600 for some of the standard AGM batteries) or the Energels in 2V 650Ahr or 2V 1000Ahr varients depending on if a fixed solar site or a trailer.

We have recently bought 2 x Christie Engineering diesel chargers which are rated at 14.0 - 14.8V @ 120A as a redundant system for our Comms sites at mines. We run 15 - 20 x 80W panels, 200 or 400W AirX wind generator and the 120A diesel autostart charger which is controlled by the solar reg (PL60 in most cases). The diesel chargers are my first experience in this area so am keen to get one going for testing.

I will buy in a MPPT reg next week to have a play with as they are supposed to be 20% more efficient than a standard reg so am interested to see how they stack up. Also you can get them in ratings of 60A plus which is great for a site with several repeaters and 30 odd panels (no more splitting into banks and doubling up on equipment). Just have to check up on the specs.

What ones do you use?

We have done a couple of 48V sites using same equipment (Christies Charger & panels but no wind gennie) with good results.

Today I just ordered a Christies 12V petrol charger (5.5 Honda 4 stroke rated at 14.0 - 14.8V @ 120A) so that I am not sitting at a site with the car connected for 4 hours twiddling my thumbs. I hope this will speed things up quite a bit and will accompany me on every callout to a solar site from now on. They follow the same principle you describe of running at higher voltages but have the advantage of a high / low switch to adjust voltage to suit wet cell or AGM batteries.

Great to see someone who has been there and experienced all the joys of solar powered solutions. The only real way to learn is to get in there and experiment with different things.

I love this stuff cause I get to design it, install it and see it work well but can also use it when I go out camping.

Regards
David
0
FollowupID: 616120

Follow Up By: RV Powerstream P/L - Friday, Feb 06, 2009 at 21:16

Friday, Feb 06, 2009 at 21:16
David
What DOD are you considering with your cycling figures as the Energel have been tested by CSIRO at 1200 x100% DOD and if your only cycling 25% that would go out to 4800.

The Hayes Gel claims to be the highest with just over 400 cycles at 80%DOD and good AGM 's are around that figure although Ive seen some 300AH AGMs murdered in a high machanical charge and discharge situartion in around four months.

I use Blue Sky and the maximum is up to 30% but that relates to a winter climate which is when you want the extra but overall you should get around 15% but is a bonus and cheaper that an extra panel.

Regards
Ian


0
FollowupID: 616129

Follow Up By: Grungle - Saturday, Feb 07, 2009 at 13:45

Saturday, Feb 07, 2009 at 13:45
Ian, We design our systems around 70% DOD based on around 20 - 30% duty cycle for the repeaters.

A decent emergency can change that though and the duty cycle will climb to 100% (emergency alarm being constantly transmitted) which will drop the DOD pretty quickly. If there is any bad weather around, it will keep dropping hence the need for a backup system.

For non-commercial applications I think 400 cycles is about right if you look after your batteies. However for commercial systems, we try for 7 - 10 years as it gets very expensive when forking out $4k - $5k just for batteries.

We don't do 4wd's or campers / caravans as it is too hard to compete with the likes of Battery World and the like so we stick with the commercial side. We do look after our local 4wd club members though and I have built a decent system for the camper which I always keep tweaking.

Regards
David
0
FollowupID: 616230

Follow Up By: RV Powerstream P/L - Saturday, Feb 07, 2009 at 17:46

Saturday, Feb 07, 2009 at 17:46
David
Good on you.
So basically your cycles are based on say 30% DOD.

Its a hard sell convincing people about quality batteries but we have quite a few vehicles out there with RV Gel and one 5th wheeler in particular a Dryden is set up with 6x650AH x2volt in the van 2x200AH x6volt as the tow aux plus crankers as normal and can run his air con on batteries and rang me from Katherine one Sunday lunchtime saying

"Ive just stopped for lunch in the main street of Katherine and its stinking hot outside so Im lunching in the van with the air con on."

I was please but bloody very envious.

We can do US Coast Guard & ABYC approved Battery Boxes with gel to give 200AH12V with 6V cells ,310AH 12V with 4V cells 450Ah with 2V cells and 650AH with 2V cells.

If people use two twelve volt and or expensive AGM's even through Battery World we can offer a deal and in a designed system a 5year warranty.
Most batteries now for deep cycle use have a 6Months warranty.

I better shut up as I am hijacking the thread.

Regards
Ian







0
FollowupID: 616263

Follow Up By: RV Powerstream P/L - Saturday, Feb 07, 2009 at 17:47

Saturday, Feb 07, 2009 at 17:47
Sorry Lunchbucket.
ian
0
FollowupID: 616264

Reply By: RV Powerstream P/L - Thursday, Feb 05, 2009 at 17:16

Thursday, Feb 05, 2009 at 17:16
15.1V and I doubt the Electro will get there.
It is made by Manson Engineering of Hong Kong and good but I do not think they have included Calcium charging as yet.
Ian
AnswerID: 347703

Reply By: lunchbuckett - Thursday, Feb 05, 2009 at 19:47

Thursday, Feb 05, 2009 at 19:47
thank you and everyone for there advise looks like back to drawing board cheers
AnswerID: 347722

Reply By: Member - Pesty (SA) - Friday, Feb 06, 2009 at 19:12

Friday, Feb 06, 2009 at 19:12
Lunchy,

I cant be happier with my 25A C Teck battery charger, best charger on the market for calcium, gell and flood batteries.
Have been using calcium batteries for years and never been able to get them charged as well as I can now, and now I have some gell batteries to throw into the mix as well.
Am going to buy another one, maybe 7 amp to keep the camper batteries topped up.

Cheers Pesty
AnswerID: 347878

Follow Up By: RV Powerstream P/L - Friday, Feb 06, 2009 at 21:24

Friday, Feb 06, 2009 at 21:24
Pesty
Unless the Ctec has had a charge regime recently installed for calcium I doubt that it can fully charge them and I state that as new chargers coming out now with a specific Calcium selection are stating 15.1V.

The Ctec in my opinion (which means ziff) is not the best but is reasonable value for money.
Ian
0
FollowupID: 616132

Follow Up By: lunchbuckett - Friday, Feb 06, 2009 at 21:50

Friday, Feb 06, 2009 at 21:50
Pesty Ian is correct in that the hi-tec will not charge calcium battery fully. my complaint with them is they carnt take the heat and they dont start correctly all the time cheers
0
FollowupID: 616134

Follow Up By: RV Powerstream P/L - Monday, Feb 09, 2009 at 12:34

Monday, Feb 09, 2009 at 12:34
The only one I have seen so far is the new Sterling Combi Q and S Inverter Chargers that have a designated charge selection for Calcium and that is 15.1V but unless you wanted a 1600W inverter along with a charger its a bit expensive.
Ian
0
FollowupID: 616521