qldcamper ........ heh heh .. ..... mate Ive been dealing with batteries large and small most of my working life ..... yes I have been formally trained and I try my best to keep up with the issues.
while there are some matters of personal opinion and there are many strongly held just plain wrong beliefs about batteries ..... the issues of series and parallel battery banks are very
well known, very
well documented and not a matter of opinion.
It is very
well known that in a single supply situation, it is by far better to use a series bank of batteries than a parallel bank.
In my apprenticeship we where trained on and maintained very large banks combined in series and parallel in battery rooms bigger than most peoples lounge room..... these batteries where supervised extrordinarily stringently, with voltages and SG of individual cells taken and recorded weekly ...... the informaion and polocies of this organisation alone where built on decades of records over thousands of sites ....... I think they knew what they where doing when they trained me over 30 years ago.
In more recent times I have had experience with lead acid batteries from 1.2Ah to 200Ah on a regular bassis ..... on a busy day of preventive maintenence these days I will
test and or replace batteries on between 8 and 15 sites in a day.
I don't claim to know it all ....... but I have a pretty good "background" knoweledge.
The issues of series and parallel banks are very
well known as I said.
IN ALL batteries of all types no two batteries or cells are identical or have identical charge discharge behaviours.
In a series bank ... .... ALL standard off the shelf lead acid family packages BTW are series banks of cells if they are not single 2 volt cells.
In a series bank of cells .... current that flows flows equally thru all cells ..... without question ...... thus the whole bank load shares equally the entire life of the battery ........ individual cells WILL charge and discharge at slightly differing rates ..... but in series as long as the bank is fully charged those cells will equalize.
In a parallel bank of batteries ........ the two banks WILL NEVER (in lead acid,can't won't does not happen) load share equally ...... if the wiring is correctly configured and the batteries are
well matched, this can be done with reasonable results but ....... one bank WILL ALWAYS take more load than the other ........ as the batteries age this will get worse and worse ...... maximum life WILL NEVER be achieved out of either battery.
In bad cases one battery will fail long before the other and
well before it's best life ..... in bad cases the failing battery will will prevent the better battery from charging and or take it with it.
what automotive manufacturers do with batteries and electrics in general can not be held up as best practice ...... there are many priorities before best battery practice. ....... in some casses they simply did not have space for a big enough battery or in the case of landcruiser, (it is commonly argued) the single battery did not have sufficient capacity to crank in cold climates, so a second was fitted.
Most Japanese trucks run 24 volt systems and run 2 x 12 volt or 4 x 6 volt banks as factory fitted. Likewise many european trucks and busses.
Many of the American trucks , Mack, Kenworth, Freightliner run 12 volt systems with some with parallel batteries.
WHY they try to crank 12 litre diesel engines off a 12 volt system is beyond me ..... yes and most these days ARE electric crank.
Some models of Freightliner, run a 4 x 12 volt in paralell battery rig ..... this battery carrier runs the full width of the truck just behind the front wheels ....... the positive comes in one end and the negative in the other with a very heavy loom connecting all 4 batteries.
INvariably ..... 2 of the 4 batteries fail long before the other two.
It is
well known,
well proven and
well documented, over many decades, that a series combination of batteries is by far a better option than a paralell arrangement if it can be implimented.
cheers