Sunday, Apr 27, 2014 at 13:12
Bantam,
I do not wish to contribute to hijacking the original topic and becoming involved in an extensive argument but in the interests of fidelity I will answer you by responding to your points as follows:
1. "By law there is no earth neutral bond in a caravan."
Agreed, and there does not need to be. The Wiring Rules define the specific arrangement of intentional connection between the neutral conductor and earth. In general, this is at one point only in an "installation" at main switchboards. A caravan is not an 'installation' and the distribution board within a caravan is not a main switchboard.
As a generalisation, it is not functionally necessary for an "earth-neutral" bond to be installed in an installation for a RCD to effectively protect. All that is required is an alternate return current path which may be provided elsewhere or unintentionally by a fault connection. Without such path, no current will flow to earth and an RCD will not trip, but then neither can an electric shock occur as no current flows.
2. "There can be no in ballance (sic, read 'imbalance') and the can be no current flowing in the earth if there is no connection between the neutral and the earth."
The original question was in regard to supply from a battery-driven inverter which can be assumed to be fully isolated, i.e. no intentional connection between its live conductors and earth.
In this situation there is no current path and no risk of electric shock due to a person contacting one live conductor and earth. Accordingly, the issue of imbalance does not arise.
3. "There is a vague discription of how the device works on the site but no detailed explanation."
There are technically adequate descriptions of the product on the Safelec website. Your inability to discover them does not mean that they are not there.
4. "No doubt this device will achive greater sensitivity, particularly under dertain circumstamnces. but it can not possibly protect against an active to neutral shock."
No one has claimed that it will protect against active to neutral shock, and incidentally, neither will an RCD or anything else.
5. "If there is no earth neutral bond and there is no connection with the greater mass of earth.....for all inetents and purposes, there IS no earth........."
Certainly, there "IS no earth" as you describe. That is, there is no deliberate connection between a live conductor and earth, but a 'first fault' occurrence can produce such a connection. In this event it is possible for personal contact between the other live conductor and earth to create an electric shock. The presence of a RCD correctly positioned in the circuit would detect an unbalanced current flow and interrupt the supply. An MEN type connection is not a requirement in such situation.
6. ".....many of the modes of shock become active to neutral path."
In point of fact, it is rare that persons become in contact simultaneously with the active and neutral conductors. And there is no current method available to safeguard from such event.
7. "There is just no way arround it.....so much of what we take for granted in the electrical safety in our homes relies on an earth neutral bond and a connection to the greater mass of earth."
The "earth neutral bond" or MEN is not necessary for valid operation of an RCD. If the return current is unequal to the supply current then the RCD will trip. Any difference in these currents indicates that its return to the source is abnormal and possibly through a human body. The return current (or part of it) does not need to be via the installation but can be any alternate path to the source. The incorporation of RCD's is not reliant on the MEN system which has its own benefits and reasons for adoption that are too extensive to discuss here.
8. "NOW..these RVDs may work when the RCD is included in the inverter or generator, because there will be an earth-neutral bond in that generator or inverter."
Totally incorrect. The RVD is not reliant on a RCD or earth-neutral bond within the inverter or generator. This particular RVD does utilise connection to a RCD but only to use it as a convenient circuit breaker to be tripped by the RVD. It can just as easily have a circuit breaker incorporated within the RVD.
9. "But if it is a generaotor with no RCD built in there will be no earth neutral bond and the RCD in the caravan will not work."
If the RVD were installed in conjunction with the RCD in the caravan then the caravan wiring would be protected as intended by the RVD tripping the RCD breaker. Installed earth to neutral bonds have nothing to do with it.
The following reproduction of a diagram from the Safelec website reveals the method of installation and operation of the product. It can be seen how the tripping circuit connects to the terminals of the RVD. More information exists on their pages and can be viewed with just a little endeavour. I am disinclined to further this discussion to avoid a prolonged argument, so Bantam, you may have the final volley if you so wish.
Safelec diagram
FollowupID:
814334